消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

机械消防排烟问题

建筑防火设计规范8.5.4条,无窗房间指的是外窗么?如果是内区房间,有内窗与其它有机械排烟的空间连通,能否不做排烟?

消防网友76458 | 2020-12-08 11:40
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

PQ 2020-12-08 17:16 00 [回复]举报

是指外窗,内窗不可以的。

潘天坤 2024-06-22 06:28 00 [回复]举报

暖通上对于无窗房间的定义一般为无可开启外窗的房间

内窗一般不能作为排烟设施

房间没有设置门或者隔墙没有隔到顶,与有设置机械排烟的空间连通,这种情况该机械排烟的防烟分区面积计算应把此房间面积算上,计算排烟量也是如此

李勤 2025-06-17 16:32 00 [回复]举报

不可以,指的是可靠的外窗。

关闭

关闭

手机APP下载